Problem about baseline controller of NREL 5MW wind turbine

Postby Yanhua.Liu » Tue Jul 05, 2016 3:49 pm

Hi all,

I am trying to design baseline torque controller and pitch controller as the description of Chapter 7.2 and 7.3 of this Pdf " http://www.nrel.gov/docs/fy09osti/38060.pdf" .Now I have some confusion about the baseline torque controller. The curve between generator torque and generator speed is like the blue one in Figure 1
Figure 1.jpg
Figure 1.jpg (79.25 KiB) Viewed 1757 times
. I set the wind speed is a constant 18m/s and results are obtained like in Figure 2. You can see the generator power and torque both have some fluctuation at near 11s -16s which is caused by the little fluctuation of the rotor speed. I found this is because when the generator speed vibrates lightly between region 2 1/2 and region 3, the output torque and power have a big fluctuation showed in Figure 2
Figure 2.jpg
Figure 2.jpg (74.01 KiB) Viewed 1757 times
. I think the fluctuation of generator power like in Figure 2 is caused by the region 2 1/2. What's the purpose of the region 2 1/2?

Because the above problem, when I set the wind speed as changing, the generator power fluctuated too much like in Figure 3
Figure 3.jpg
Figure 3.jpg (87.74 KiB) Viewed 1757 times
. Can anyone help me to explain or solve this problem? It drives me crazy. Thank you so much!

All the best.

Yanhua

Jason.Jonkman
Posts: 3753
Joined: Thu Nov 03, 2005 4:38 pm
Location: Boulder, CO
Contact:

Re: Problem about baseline controller of NREL 5MW wind turbi

Postby Jason.Jonkman » Wed Jul 06, 2016 1:39 pm

Dear Yanhua,

Region 2 1/2 exists to limit tip speed (and hence noise emissions) at rated power i.e. without it, rated power would not be reached until a much higher speed.

To eliminate the drastic drops of torque and power in Region 3, the NREL 5-MW baseline controller places uses a conditional statement so that the torque is computed as if it were in Region 3--regardless of the generator speed--whenever the blade-pitch-angle command exceeds 1 deg, as explained in Section 7.2 of the NREL 5-MW specifications report that you referenced.

I hope that helps.

Best regards,
Jason Jonkman, Ph.D.